Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Moderator: Moderators
- TWDB
- Snr Member
- Posts: 391
- Joined: Thu Apr 11, 2013 3:24 pm
- 11
- Industry Sector: Civil Eng, HV Elec, Remediation Soil/Wat
- Occupation: SHEQ Manager
- Location: UK WIDE
- Has thanked: 177 times
- Been thanked: 29 times
Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Hi all,
I am having a discussion with a client about if a cable strike is reportable as dangerous occurrence under RIDDOR
I have reviewed the below and say not if the following apply (from HSE website and RIDDOR.
"Q. An underground electricity cable was struck, causing a bang and a flash-over. We were told by the distributor that it is below 230 V. Is it reportable?
A. It depends on the circumstances, and you need to use a degree of judgement. The cable is 'plant', and a short-circuit occurred when the cable was struck, causing the bang and flash-over (explosion). However, the incident would not be reportable if the cable was repaired within 24 hours, and there was no potential for any person to die.
The incident would be reportable if:
it took longer than 24 hours to repair the cable
the explosion had the potential to cause fatal injuries
the cable was energised at a voltage high enough to cause electrocution, and a person holding a conducting object such as a metal tool struck it
Please note:
Contact with the energised exposed conductors of an electrical cable or circuit operating above 50 V alternating current (ac) or 125 V direct current (dc) could cause death by electrocution.
A mechanical tool penetrating an energised electric power cable will create a short-circuit either between two or more of the phase conductors within the cable or between the outer earthed armouring of the cable and one or more of the phase conductors within the cable.
an example made where it would be reportable as a dangerous occurrence - was that if cable is struck by a machine (360) then it would be reportable as a dangerous occurrence - cable being 415Volt
any thoughts and comments welcome.
T
I am having a discussion with a client about if a cable strike is reportable as dangerous occurrence under RIDDOR
I have reviewed the below and say not if the following apply (from HSE website and RIDDOR.
"Q. An underground electricity cable was struck, causing a bang and a flash-over. We were told by the distributor that it is below 230 V. Is it reportable?
A. It depends on the circumstances, and you need to use a degree of judgement. The cable is 'plant', and a short-circuit occurred when the cable was struck, causing the bang and flash-over (explosion). However, the incident would not be reportable if the cable was repaired within 24 hours, and there was no potential for any person to die.
The incident would be reportable if:
it took longer than 24 hours to repair the cable
the explosion had the potential to cause fatal injuries
the cable was energised at a voltage high enough to cause electrocution, and a person holding a conducting object such as a metal tool struck it
Please note:
Contact with the energised exposed conductors of an electrical cable or circuit operating above 50 V alternating current (ac) or 125 V direct current (dc) could cause death by electrocution.
A mechanical tool penetrating an energised electric power cable will create a short-circuit either between two or more of the phase conductors within the cable or between the outer earthed armouring of the cable and one or more of the phase conductors within the cable.
an example made where it would be reportable as a dangerous occurrence - was that if cable is struck by a machine (360) then it would be reportable as a dangerous occurrence - cable being 415Volt
any thoughts and comments welcome.
T
Update: taken a new job hopefully confidence and positivity will return with new challenge - scary though leaving current place after 16 years (6 years H&S !)
(previous signature: was motivated once ..................... searching to get it back ! )
(previous signature: was motivated once ..................... searching to get it back ! )
- Alexis
- Official HSfB Legend
- Posts: 48861
- Joined: Thu Mar 18, 2004 10:52 am
- 20
- Twitter: https://twitter.com/AlexisHSfB
- Location: West Lothian
- Has thanked: 2850 times
- Been thanked: 340 times
- Contact:
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Bump
"A candle loses none of its light by lighting another candle."
Hundreds of FREE Health & Safety Downloads Here
Hundreds of FREE Health & Safety Downloads Here
- Safety
- Grand Shidoshi
- Posts: 2024
- Joined: Wed Mar 12, 2008 10:37 am
- 16
- Industry Sector: Food Manufacturing Industry
- Occupation: Health and Safety Manager
- Location: Going to see the Wizard of Oz!
- Has thanked: 1 time
- Been thanked: 63 times
- Contact:
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Cable strikes
Incidents involving cable strikes are reportable as this involves one of the defined dangerous occurrences. However, the HSE makes it clear that “it depends on the circumstances, and you need to use a degree of judgment”. In this instance, the cable would be considered “plant” and the incident involves electricity. If the cable was repaired within 24 hours of the strike and “there was no potential for any person to die”, it would not be reportable.
However, if the voltage was high enough to cause electrocution and a person was holding a metal tool, for example, it would be reportable as a dangerous occurrence if, say:
any resulting explosion had the potential to cause fatal injuries
it took longer than 24 hours to repair the cable.
It should be noted that this relates to the potential for injury. Clearly, if the person was killed, the fatal injury procedure would apply.
Incidents involving cable strikes are reportable as this involves one of the defined dangerous occurrences. However, the HSE makes it clear that “it depends on the circumstances, and you need to use a degree of judgment”. In this instance, the cable would be considered “plant” and the incident involves electricity. If the cable was repaired within 24 hours of the strike and “there was no potential for any person to die”, it would not be reportable.
However, if the voltage was high enough to cause electrocution and a person was holding a metal tool, for example, it would be reportable as a dangerous occurrence if, say:
any resulting explosion had the potential to cause fatal injuries
it took longer than 24 hours to repair the cable.
It should be noted that this relates to the potential for injury. Clearly, if the person was killed, the fatal injury procedure would apply.
The light at the end of the tunnel has been turned off due to budget cuts..............
- TWDB
- Snr Member
- Posts: 391
- Joined: Thu Apr 11, 2013 3:24 pm
- 11
- Industry Sector: Civil Eng, HV Elec, Remediation Soil/Wat
- Occupation: SHEQ Manager
- Location: UK WIDE
- Has thanked: 177 times
- Been thanked: 29 times
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Thanks both
Update: taken a new job hopefully confidence and positivity will return with new challenge - scary though leaving current place after 16 years (6 years H&S !)
(previous signature: was motivated once ..................... searching to get it back ! )
(previous signature: was motivated once ..................... searching to get it back ! )
- witsd
- Grand Shidoshi
- Posts: 1087
- Joined: Tue Nov 18, 2014 4:37 pm
- 9
- Occupation: Fire safety officer
- Location: Glasgow
- Has thanked: 91 times
- Been thanked: 265 times
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
My standard go-to answer:
Unless you are having tons of these*, then it's faster to just report the single incident than to spend ages working out if you have to report it. It won't cause HSE to descend upon you from a great height - most likely you'll never hear a peep.
*If you are having tons of these, then obviously it should be reported as sooner or later someone is going to come to serious harm.
Unless you are having tons of these*, then it's faster to just report the single incident than to spend ages working out if you have to report it. It won't cause HSE to descend upon you from a great height - most likely you'll never hear a peep.
*If you are having tons of these, then obviously it should be reported as sooner or later someone is going to come to serious harm.
We often think that when we have completed our study of one we know all about two, because 'two' is 'one and one.' We forget that we still have to make a study of 'and.'
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Stupid question related to cable strikes but not necessarily reportable cable strikes.
Would driving over an armoured cable in a Mewp and damaging the cable be classed as a cable strike? I am under the impression that cable strikes only relate to buried cable?
I am a fledgling H&S advisor and we have been asked by our client, to carry our a full investigation after a Mewp drove over an armoured cable, damaging the cable and outing the power to the site and offices. The site is a small 2 storey school FYI
Any help would be appreciated
PD
Would driving over an armoured cable in a Mewp and damaging the cable be classed as a cable strike? I am under the impression that cable strikes only relate to buried cable?
I am a fledgling H&S advisor and we have been asked by our client, to carry our a full investigation after a Mewp drove over an armoured cable, damaging the cable and outing the power to the site and offices. The site is a small 2 storey school FYI
Any help would be appreciated
PD
- Alexis
- Official HSfB Legend
- Posts: 48861
- Joined: Thu Mar 18, 2004 10:52 am
- 20
- Twitter: https://twitter.com/AlexisHSfB
- Location: West Lothian
- Has thanked: 2850 times
- Been thanked: 340 times
- Contact:
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Many thanks if anyone can offer their advice to Paul.
"A candle loses none of its light by lighting another candle."
Hundreds of FREE Health & Safety Downloads Here
Hundreds of FREE Health & Safety Downloads Here
- WillPool
- HSfB Moderator
- Posts: 10810
- Joined: Mon Mar 13, 2006 8:45 pm
- 18
- Industry Sector: Construction/Civils/Telecomms
- Occupation: Regional Safety Director
- Location: Tabuk - Saudi Arabia
- Has thanked: 25 times
- Been thanked: 326 times
- Contact:
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
It is better to be careful 100 times than to get killed once.
Mark Twain (1835 - 1910)
Mark Twain (1835 - 1910)
- Alexis
- Official HSfB Legend
- Posts: 48861
- Joined: Thu Mar 18, 2004 10:52 am
- 20
- Twitter: https://twitter.com/AlexisHSfB
- Location: West Lothian
- Has thanked: 2850 times
- Been thanked: 340 times
- Contact:
Re: Question: Under RIDDOR are all cable strikes reportable as a Dangerous occurrence?
Thank you Will.
"A candle loses none of its light by lighting another candle."
Hundreds of FREE Health & Safety Downloads Here
Hundreds of FREE Health & Safety Downloads Here