Frequency of testing and inspection part deux

Post by stephen1974 »

Just visited a place that has no electronic fire alarm in terms of an alarm panel, detectors and call points, but it does have 3 smoke detectors that are linked together, so if one sounds they all sound.

It was unclear if the systems were purely battery operated or if they were powered from the mains. So not sure if its a class D or a class F system.

BS-5839-6 seems to suggest weekly testing but no 6 monthly service required.

Would monthly not be ok?

I have the lovely situation of a previous advisor telling a customer one thing, and then me telling them something different a year later after the other guy has left. They are pretty decent about things but minimum required standards seem to be the order of the day.
User avatar
bernicarey
Anorak Extraordinaire
Anorak Extraordinaire
Posts: 8973
Joined: Tue Jan 13, 2009 2:50 am
15
Twitter: @bernicarey
Industry Sector: Consultancy/Training
Occupation: Safety, Health, Environment and Fire Consultant.
Location: The heart of the East Midlands...
Has thanked: 76 times
Been thanked: 300 times
Contact:

Re: Frequency of testing and inspection part deux

Post by bernicarey »

From your own description, you've identified it to be either a D1/D2 or an F1/F2 system, so why do you say
BS-5839-6 seems to suggest weekly testing but no 6 monthly service required.
.scratch


BS5839-6:2019 says

Grade A should be tested weekly; all others at least every month.

As for maintenance, if Grades C, D1/2 or F1/2 are in a sheltered housing situation, then it's every 12 months, otherwise not applicable.
See Table 3 of BS5839-6:2019.

Even if 12 monthly is to be carried out, it's only by a competent person and it's pretty basic.
www.belvoirsafety.co.uk

Tomorrow - your reward for being safe today...

Image
stephen1974
Anorak Extraordinaire
Anorak Extraordinaire
Posts: 743
Joined: Fri Aug 02, 2013 1:55 pm
10
Has thanked: 26 times
Been thanked: 202 times

Re: Frequency of testing and inspection part deux

Post by stephen1974 »

The standard says:

Grade B and Grade C systems should be serviced every six months in
accordance with the supplier’s instructions.

Smoke alarms in Grade D, Grade E and Grade F systems should be cleaned
periodically in accordance with the manufacturer’s instructions.
User avatar
bernicarey
Anorak Extraordinaire
Anorak Extraordinaire
Posts: 8973
Joined: Tue Jan 13, 2009 2:50 am
15
Twitter: @bernicarey
Industry Sector: Consultancy/Training
Occupation: Safety, Health, Environment and Fire Consultant.
Location: The heart of the East Midlands...
Has thanked: 76 times
Been thanked: 300 times
Contact:

Re: Frequency of testing and inspection part deux

Post by bernicarey »

stephen1974 wrote: Fri Feb 07, 2020 1:42 pm The standard says:

Grade B and Grade C systems should be serviced every six months in
accordance with the supplier’s instructions.

Smoke alarms in Grade D, Grade E and Grade F systems should be cleaned
periodically in accordance with the manufacturer’s instructions.
Does it really..... Well no it doesn't actually. There was/is a reason I quoted BS5839-6:2019

Note the 2019 bit! It was updated last April.

For example, No such thing as a Grade B or a Grade E in the latest version.
Also why I quoted D1/D2 or an F1/F2 and not just D or F as you had done, because they are both now split.

Much like the First Rule of Fight Club is "Don't talk about Fight Club"...
First Rule of Quoting References is 'Make sure you've quoting the right one'!
www.belvoirsafety.co.uk

Tomorrow - your reward for being safe today...

Image
User avatar
Messy
Grand Shidoshi
Grand Shidoshi
Posts: 3585
Joined: Wed Dec 27, 2006 8:59 am
17
Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.

Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment
Location: Sunny London where the streets are paved with gold ;)
Has thanked: 363 times
Been thanked: 660 times

Re: Frequency of testing and inspection part deux

Post by Messy »

Stephen. Out of interest, was this premises residential or commercial??