Hello,

I hope someone could help me on this. We have around 233 venues around the UK each obviously have fire doors in them which are checked by venue staff monthly for their operation/strips intact etc and then a annual service by a outside company.

The company has stated that due to BS 9999 these fire doors should be tested every 6 months instead of annually.

Can anyone shine some light on this as being honest I thought what we are currently doing is enough.

Thanks

Mark .salut
User avatar
Messy
Grand Shidoshi
Grand Shidoshi
Posts: 3588
Joined: Wed Dec 27, 2006 8:59 am
17
Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.

Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment
Location: Sunny London where the streets are paved with gold ;)
Has thanked: 369 times
Been thanked: 663 times

Re: Fire Doors

Post by Messy »

Tested? Not inspected?

It may be semantics but I would want to know which bit of 9999 is being referred to. Sadly it's a bit weighty for me to lug a copy on the train, but I would want a reference or rationale
User avatar
bernicarey
Anorak Extraordinaire
Anorak Extraordinaire
Posts: 8973
Joined: Tue Jan 13, 2009 2:50 am
15
Twitter: @bernicarey
Industry Sector: Consultancy/Training
Occupation: Safety, Health, Environment and Fire Consultant.
Location: The heart of the East Midlands...
Has thanked: 76 times
Been thanked: 300 times
Contact:

Re: Fire Doors

Post by bernicarey »

Why are you having an external company doing an 'annual service' of Fire Doors?

Do they include automatic release systems etc, or are they just fire doors?

Have you looked at the requirements of BS9999 yourself?

Yes, there is a requirement for a 6 monthly inspection, but it seems to me that your staff are already potentially meeting that requirement in their monthly checks....

Link via Manchester Reference Library: https://bsol.bsigroup.com/PdfViewer/Vie ... 0030357099

Annex I
page 350
Six Monthly.JPG
www.belvoirsafety.co.uk

Tomorrow - your reward for being safe today...

Image
User avatar
witsd
Grand Shidoshi
Grand Shidoshi
Posts: 1086
Joined: Tue Nov 18, 2014 4:37 pm
9
Occupation: Fire safety officer
Location: Glasgow
Has thanked: 90 times
Been thanked: 264 times

Re: Fire Doors

Post by witsd »

As long as you are recording your monthly checks clearly, I don't see how doing additional annual / six-monthly checks adds any value.

It doesn't take a degree in rocket science to identify a missing intumescent strip, a large gap, or note that the door is failing to self-close.

Unless these doors are connected to the fire alarm system and swing shut upon activation (which can be easily checked during fire alarm tests), I don't see what the external company would be doing that your staff wouldn't.