Escape Windows - residential flat

Post by Paul1979 »

Hi All,  

Please can I ask for your opinion on a property which is a 2 storey flat which sits above a commercial unit (shop)?

High street property is built in 1800's. Standard construction (Brick, timber floors, etc). Plasterboard ceiling separates shop and flat above. Alarm in shop is also linked to sounder in flat. The flat is found on first and second floor levels. There is one doorway to access the flat.

The entrance to the flat is found to the rear of the property and is accessible via a steel external stairway and small flat roof area.  The door at first floor also serves as the only external door opening to fresh air.  BUT, it also opens directly in to the kitchen!  :shock: So, tenants (a young family with autistic child) are understandably worried they have to pass through the kitchen to escape.   :(

We are prepared to tell the landlord we need to reconfigure the flat to avoid occupants having to go through the kitchen, but looking at all options, would you commonly accept an escape window on the first floor level on the first floor as long as it meets the standard requirements of size (450mm x 450mm) and is no more than 4.5m from ground level? The second floor is the mum and dads bedroom and they can travel down to the first floor to access the escape window which is in the living room / lounge and drops down to the high street pavement level.

In addition to the escape window, we are looking at fitting FD30s door-set to kitchen and increase alarm coverage to LD2 category.

But would under any circumstances you accept a kitchen as an access room to the exit?? Suppression system maybe??

Any steer / advice always appreciated and comments taken on board. .salut
"If life were predictable it would cease to be life and be without flavor." ../.
User avatar
Waterbaby
HSfB Moderator
HSfB Moderator
Posts: 4714
Joined: Sat Jul 23, 2011 10:53 am
12
Industry Sector: Medical
Location: Ireland
Has thanked: 216 times
Been thanked: 472 times

Re: Escape Windows - residential flat

Post by Waterbaby »

Bump ./thumbsup..

WB
#DrowningPrevention, #RespectTheWater
User avatar
Messy
Grand Shidoshi
Grand Shidoshi
Posts: 3588
Joined: Wed Dec 27, 2006 8:59 am
17
Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.

Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment
Location: Sunny London where the streets are paved with gold ;)
Has thanked: 369 times
Been thanked: 663 times

Re: Escape Windows - residential flat

Post by Messy »

Domestic fire safety.issues that relate to a means of escape within a flat (as opposed to fron common area) is not an area I specialise in.

Escape windows for lofts are not recommended by building regs now, so I cannot see one being permitted here . As for escape through a kitchen, that was not allowed , but u see a number of modern single level flats where bedrooms are accessed from the kitchen

Is the behaviour of the child likely to raise the risk of fire? If so, it might be the case that it's inappropriate to rent this property
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Escape Windows - residential flat

Post by Paul1979 »

Hi messy, the window we are looking at using for means of escape is on first floor and is less than 4.5m in height from pavement level at front. Looking at the new ADB volume 1 this appears satisfactory?
"If life were predictable it would cease to be life and be without flavor." ../.
User avatar
witsd
Grand Shidoshi
Grand Shidoshi
Posts: 1086
Joined: Tue Nov 18, 2014 4:37 pm
9
Occupation: Fire safety officer
Location: Glasgow
Has thanked: 90 times
Been thanked: 264 times

Re: Escape Windows - residential flat

Post by witsd »

Might be fine for an office staffed with able-bodied adults.

In this case, I cannot see a way to safely drop a child 4.5m onto a concrete pavement. Having watched a number of 1800s tenements with shops on ground floor levels go up VERY quickly in Glasgow over the last few years, I wouldn't be happy with the residents waiting for the FRS either.

So personally, I don't think I could condone it, even if it's technically allowed.