Paul1979 wrote: ↑Wed Nov 18, 2020 4:26 pm
My most biggest fears are 1) being unfamiliar with the Evacuator alarm system and fact it isn't BS recognised; 2) the fact that a fire could originate in one part of the buildings and the system fail to warn others in a part of the building where the products of the fire are not possible to see/smell; 3) the fear of the cables failing due to heat; 4) people (especially those wearing head phones) not hearing the alarm or seeing the visual alarms; 5) the limitation of the Evacuator alarm system not being able to include AFD; 6) having no CIE to continually monitor for faults; 7) not convinced client will ever test the alarm!
You are right though; its the FRA and lack of mention of BS5839-1 being a suitable benchmark that's causing the client to dig his heals in...I can only give them my advice to the best of my knowledge / competency I guess.
1) Yeah, this is my biggest issue here. I usually try not to get stuck with the BS – they are great when deciding what to get, but not so useful when comparing what you already have against what you actually
need. Problem here being gauging the gap between this system and a BS-compliant one.
2) This isn't
really an issue for life safety. As soon as smoke reaches a point where it could affect staff, staff should be reacting to it, and activating the alarm on their way out. Yes, AFD (of whatever type) would provide an earlier alarm and could reduce the risk a small amount though.
3) This one goes back to 1). Are BS-compliant systems significantly more resistant to heat, and if so, how much additional alarm time will that provide? Is there a realistic chance of this alarm system failing due to fire before it is activated?
4) This is a training issue, and while it is a factor worth considering, there's nothing to stop you providing an 'either/or' action e.g. "The use of earphones in work areas should be banned unless the existing alarm system is upgraded to meet BS" The beacon effectiveness would depend upon the alarms' positioning and may be inadequate, but no way for us to comment.
5) Two separate alarm systems may not be ideal, but may well reduce the risk to life to a similar level to that of one integrated system for a fraction of the cost.
6) & 7) as long as the FRA is specifying that alarm tests must be completed weekly, then this is largely out of your hands but could be addressed similarly to 4) – "The testing regimen must be adhered to. Any deviation from this should be taken to indicate that a BS-compliant alarm system with automated fault identification is required at this site."
But certainly the safest and easiest (for you) method is to simply say "Given the use of earphones, machinery, lack of fire drills, lack of AFD etc., it is considered that the existing fire alarm system is not adequate and should be replaced with a system that meets the current BS".
We often think that when we have completed our study of one we know all about two, because 'two' is 'one and one.' We forget that we still have to make a study of 'and.'