Flash point of dust?
In one of our processes we grind LDPE granules into powder. during this a fair amount of dust is created. Whilst I can get all the information on the properties of the granules in the condition we buy them in, how would I establish the flash point of the dust so I can do a thorough fire and DSEAR risk assessment?
So when the whole world is safe..............what are we going to do then?
- Messy
- Grand Shidoshi
- Posts: 3585
- Joined: Wed Dec 27, 2006 8:59 am
- 17
- Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.
Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment - Location: Sunny London where the streets are paved with gold ;)
- Has thanked: 363 times
- Been thanked: 660 times
- bernicarey
- Anorak Extraordinaire
- Posts: 8973
- Joined: Tue Jan 13, 2009 2:50 am
- 15
- Twitter: @bernicarey
- Industry Sector: Consultancy/Training
- Occupation: Safety, Health, Environment and Fire Consultant.
- Location: The heart of the East Midlands...
- Has thanked: 76 times
- Been thanked: 300 times
- Contact:
Re: Flash point of dust?
I think the problem is that the MSDS give a Flashpoint of the granules as they provide them.
The dust explosion risk is variable dependant on the granule size of the dust, and the amount of it in the air/dust mixture.
It's not the 'Flashpoint' you're seeking; it's the Lower Explosive Limit (LEL) and the Upper Explosive Limit(UEL), of the size of dust you're creating. For example the MSDS that messy has found doesn't give LEL/UEL because the granules don't have one.
I think it needs a Laboratory to assess the size of dust you're creating and to establish the LEL/UELs that exist.
The dust explosion risk is variable dependant on the granule size of the dust, and the amount of it in the air/dust mixture.
It's not the 'Flashpoint' you're seeking; it's the Lower Explosive Limit (LEL) and the Upper Explosive Limit(UEL), of the size of dust you're creating. For example the MSDS that messy has found doesn't give LEL/UEL because the granules don't have one.
I think it needs a Laboratory to assess the size of dust you're creating and to establish the LEL/UELs that exist.
- Keith1983
- Suitable and Sufficient since 1983
- Posts: 8330
- Joined: Mon Dec 08, 2008 3:08 pm
- 15
- Industry Sector: Engineering/Manufacturing/ Construction
- Occupation: H&S Coordinator
- Location: Lincolnshire / South Yorkshire
- Has thanked: 34 times
- Been thanked: 24 times
Re: Flash point of dust?
You're exactly right, in regards to the LEL / UEL berni! I think I was at the point of not being able to see the forest for the trees, with this one!
So when the whole world is safe..............what are we going to do then?
- bernicarey
- Anorak Extraordinaire
- Posts: 8973
- Joined: Tue Jan 13, 2009 2:50 am
- 15
- Twitter: @bernicarey
- Industry Sector: Consultancy/Training
- Occupation: Safety, Health, Environment and Fire Consultant.
- Location: The heart of the East Midlands...
- Has thanked: 76 times
- Been thanked: 300 times
- Contact: