Sprinkler systems / electrics

Post by Paul1979 »

Hi, silly question but in our office we have huge amounts of portable electrical equipment such as monitors, PC's, laptops, kettles, microwaves, photocopiers, printers, etc. A typical large open plan office.

The building is fitted throughout with a sprinkler system which is obviously a plus point!

But, is there not a risk of electrocution or other problems if the sprinkler system activates over a piece of electrical equipment that is plugged in to the mains??

Also, when does the sprinkler stop putting water on the fire?? Does it work for a certain period of time or does it automatically somehow recognise when the flames are extinguished and stop?? We're worried it may keep throwing water on the equipment in the area(s) where a fire starts which may cause other damage.

Any advice always appreciated!! .salut
"If life were predictable it would cease to be life and be without flavor." ../.
User avatar
Waterbaby
HSfB Moderator
HSfB Moderator
Posts: 4714
Joined: Sat Jul 23, 2011 10:53 am
12
Industry Sector: Medical
Location: Ireland
Has thanked: 216 times
Been thanked: 472 times

Re: Sprinkler systems / electrics

Post by Waterbaby »

Bump ./thumbsup..

WB
#DrowningPrevention, #RespectTheWater
User avatar
Messy
Grand Shidoshi
Grand Shidoshi
Posts: 3588
Joined: Wed Dec 27, 2006 8:59 am
17
Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.

Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment
Location: Sunny London where the streets are paved with gold ;)
Has thanked: 369 times
Been thanked: 663 times

Re: Sprinkler systems / electrics

Post by Messy »

Ok, risk of electrocution ?

When a sprinkler operates electrical equipment will get wet. High voltage equipment may create issues, but the appliances you mention should present a very low risk. Firstly, everyone will evacuate the wet area - trust me, it is not fun being under a sprinkler when it is full flow

Circuit breakers should provide protection, and it might be sensible to create a contingency plan of what to do if a sprinkler head did activate (real or accidentally) in respect of dealing with the water run off. The plan should include measures that you will need to take to get back in business - and staff safety when doing so. Shutting off the electric will have been done by the fire service if they attend.

Careful management of areas below sprinkler heads and regular maintenance will reduce the risk of an accidental actuation. Such events are rare. And lets dispel the Hollywood myth that when one sprinkler head activates, they all do. That is not the case for the overwhelming number of general sprinkler systems

If you have high value stock or kit - data centre or document store perhaps - a dry pipe system is available where, as the name suggests, no water enters the pipework until a fire is confirmed

Stopping the water?

Some systems use water tanks, others directly or indirectly from the mains. The water will flow until somebody turns it off!!!

If you don't know how to, you should find out as soon as possible. Again. a system should be developed to ensure care is taken not to switch the sprinklers off before the system has taken control of the fire. There are some major examples of what happens if you do this with a large computer warehouse in Hampshire during to the ground 30 years ago and Ocado's Andover warehouse ending up on the floor following the same mistake

Get some advice and plan
Sprinklers are really good news, they save lives and prevent business loss
Some systems are 100 years old and still going strong, if looked after

Search 'Fire Sprinklers Myths' for further info
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Sprinkler systems / electrics

Post by Paul1979 »

Brilliant, thank you so much messy! ;)
"If life were predictable it would cease to be life and be without flavor." ../.
User avatar
witsd
Grand Shidoshi
Grand Shidoshi
Posts: 1086
Joined: Tue Nov 18, 2014 4:37 pm
9
Occupation: Fire safety officer
Location: Glasgow
Has thanked: 90 times
Been thanked: 264 times

Re: Sprinkler systems / electrics

Post by witsd »

There's a line in an old episode of Star Trek TNG, where someone complains about an automatic fire suppression force field extinguishing their illicit campfire, asking what would have happened if they had been standing where the force field appeared.

It is quickly pointed out that that would necessitate that they were standing on top of the fire.

As Messy says, it's doubtful that anyone would hang about long enough (getting either cooked or soaked) for electrocution to be an issue.
We often think that when we have completed our study of one we know all about two, because 'two' is 'one and one.' We forget that we still have to make a study of 'and.'