Foyer sofa
Discussion Point...
A friend from a networking group has a workshop in a shared building and the landlord recently had an FRA carried out.
My fiend's business premises are on the ground floor, directly opposite the entrance.
The entrance foyer contains a sofa and occasional table, which the Assessor says must go as they are a 'Fire Risk'; my friend asked my opinion as the landlord is reluctant to remove the leather sofa.
My view is the table should almost certainly go, as a trip hazard on an escape route as much as anything else (there is about a metre gap between the table and the wall to the left, exit is to doorway on right), but as to the sofa..... You may leave comments in addition to the poll if you wish....
A friend from a networking group has a workshop in a shared building and the landlord recently had an FRA carried out.
My fiend's business premises are on the ground floor, directly opposite the entrance.
The entrance foyer contains a sofa and occasional table, which the Assessor says must go as they are a 'Fire Risk'; my friend asked my opinion as the landlord is reluctant to remove the leather sofa.
My view is the table should almost certainly go, as a trip hazard on an escape route as much as anything else (there is about a metre gap between the table and the wall to the left, exit is to doorway on right), but as to the sofa..... You may leave comments in addition to the poll if you wish....
- Jack Kane
- HSfB Site Grand Shidoshi
- Posts: 25075
- Joined: Wed Mar 17, 2004 12:13 am
- 20
- Twitter: https://twitter.com/hsfb
- Industry Sector: Manufacturing Subsea XTs
- Occupation: Senior HSE Advisor for TechnipFMC & HSfB Founder
- Location: Sunny Bo'ness
- Has thanked: 254 times
- Been thanked: 199 times
- Contact:
Re: Foyer sofa
I'm not a fire guru on here at all, but in my humble experience it looks like the risk of catching fire is kinda low. But, we can't see what's above the sofa, I'm guessing a roof with lights, so if they and their associated electrics catch fire there is a risk of falling debris. There could be a printer, tea machine, cleaner's hoover or whatever above that sofa. If they catch fire and left to do their own thing over night, the sofa won't help matters that's for sure.
I've also had an experience at one of our modern office spaces where the electrics inside the walls overheated and caught fire. There was smoke, but fire was hidden away. The fire service had to use heat detection equipment to see into the walls.
I see light switches and security swipe card systems in the hall, so electrics around somewhere.
I see a sign to keep the area clear.
I see a sofa along an emergency escape route which looks like a bit of totally unnecessary fire loading.
There's something odd about seeing flammables on an emergency escape route, I just don't like it. I also don't like the sofa
That's my thinking Unlikely scenarios, over the top? I don't care, I would move it.
I've also had an experience at one of our modern office spaces where the electrics inside the walls overheated and caught fire. There was smoke, but fire was hidden away. The fire service had to use heat detection equipment to see into the walls.
I see light switches and security swipe card systems in the hall, so electrics around somewhere.
I see a sign to keep the area clear.
I see a sofa along an emergency escape route which looks like a bit of totally unnecessary fire loading.
There's something odd about seeing flammables on an emergency escape route, I just don't like it. I also don't like the sofa
That's my thinking Unlikely scenarios, over the top? I don't care, I would move it.
RoSPA Awards Ambassador and Mentor #RoSPAAwards #HSfB #Proud
There is no such thing as a "stupid" or "daft" health and safety question!
- Messy
- Grand Shidoshi
- Posts: 3588
- Joined: Wed Dec 27, 2006 8:59 am
- 17
- Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.
Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment - Location: Sunny London where the streets are paved with gold ;)
- Has thanked: 369 times
- Been thanked: 663 times
Re: Foyer sofa
There's really insufficient information to make any sort of judgement.
If it's a single staircase premises 3 floors or more I would suggest it needs to go. Some premises have to adopt a protected route strategy. This is where travel distances to a place of ultimate safety (outside) cannot be achieved.
In these cases, you have to create places of relative safety within the building and measure your travel distance to that point. Once within a protected route, the escapee must stay in that protected environment until outside the building
A protected staircase will be enclosed in fire resisting materials, be fitted with fire doors with door closers and be kept free from combustible items and ignition sources.
Sofas in protected routes are usually discouraged. It is fair to say you need an ignition source and a combustible item to create a high risk, but for me , as a protected route is supposed to be as close to the level of safety one would find if outside the building, there are few examples where a sofa would be permitted.
If it's a single staircase premises 3 floors or more I would suggest it needs to go. Some premises have to adopt a protected route strategy. This is where travel distances to a place of ultimate safety (outside) cannot be achieved.
In these cases, you have to create places of relative safety within the building and measure your travel distance to that point. Once within a protected route, the escapee must stay in that protected environment until outside the building
A protected staircase will be enclosed in fire resisting materials, be fitted with fire doors with door closers and be kept free from combustible items and ignition sources.
Sofas in protected routes are usually discouraged. It is fair to say you need an ignition source and a combustible item to create a high risk, but for me , as a protected route is supposed to be as close to the level of safety one would find if outside the building, there are few examples where a sofa would be permitted.
- bernicarey
- Anorak Extraordinaire
- Posts: 8973
- Joined: Tue Jan 13, 2009 2:50 am
- 15
- Twitter: @bernicarey
- Industry Sector: Consultancy/Training
- Occupation: Safety, Health, Environment and Fire Consultant.
- Location: The heart of the East Midlands...
- Has thanked: 76 times
- Been thanked: 300 times
- Contact:
Re: Foyer sofa
I can add that its a 2 story brick construction, I'd estimate late 1930's build, it reminds me a lot of typical government building of the period, like many on RAF Stations I've served at in the UK.
It's an addition to a slightly older building, which was probably requisitioned to be part of a nearby WWII 'expansion' airfield hastily built in 1940/41.
I've not taken a good look at the interior, but what I have seen looks pretty bare along the corridor. Aside from carpets, that's probably the only other item in the shared spaces.
I'm not even sure of the purpose of the sofa, aside from perhaps clients waiting area. There's no refreshment facilities anywhere nearby.
It's an addition to a slightly older building, which was probably requisitioned to be part of a nearby WWII 'expansion' airfield hastily built in 1940/41.
I've not taken a good look at the interior, but what I have seen looks pretty bare along the corridor. Aside from carpets, that's probably the only other item in the shared spaces.
I'm not even sure of the purpose of the sofa, aside from perhaps clients waiting area. There's no refreshment facilities anywhere nearby.
-
- Anorak Extraordinaire
- Posts: 746
- Joined: Fri Aug 02, 2013 1:55 pm
- 10
- Has thanked: 26 times
- Been thanked: 204 times
Re: Foyer sofa
It's a large source of fuel in an escape route and it doesnt need to be there. - It's unlikely to catch fire, but what if it did? If you want seating there, there are better options. Sell the sofa for £50 and buy a couple of metal frames chairs.
Re: Foyer sofa
I agreestephen1974 wrote: ↑Wed Feb 14, 2018 9:53 pm It's a large source of fuel in an escape route and it doesnt need to be there. - It's unlikely to catch fire, but what if it did? If you want seating there, there are better options. Sell the sofa for £50 and buy a couple of metal frames chairs.
- hammer1
- Grand Shidoshi
- Posts: 2617
- Joined: Sun Oct 15, 2006 4:59 pm
- 17
- Industry Sector: Commercial, residential, construction
- Occupation: Health, Safety and Fire consultant
- Location: Sunny South London
- Been thanked: 46 times
- Contact:
Re: Foyer sofa
bernicarey wrote: ↑Tue Feb 13, 2018 5:52 pm Discussion Point...
A friend from a networking group has a workshop in a shared building and the landlord recently had an FRA carried out.
My fiend's business premises are on the ground floor, directly opposite the entrance.
The entrance foyer contains a sofa and occasional table, which the Assessor says must go as they are a 'Fire Risk'; my friend asked my opinion as the landlord is reluctant to remove the leather sofa.
My view is the table should almost certainly go, as a trip hazard on an escape route as much as anything else (there is about a metre gap between the table and the wall to the left, exit is to doorway on right), but as to the sofa.....20180213_113250.jpg
You may leave comments in addition to the poll if you wish....
The following is C&P from the fire safety guidance offices and shops;
Reception areas
Reception or enquiry areas should only be located in protected stairways where the stairway is not the only one serving the upper floors, the reception area is small (less than 10m2) and is of low fire risk.
AFD coverage needs to be assessed, is there smoke detection in this communal area? Also travel distance, if 2 storey what is the travel distance from furthest point?
In regards to robust management, obviously it conflicts with the sign and as mentioned storage of combustibles is discouraged from protected routes. Mitigate the risk by replacing as mentioned.
The song goes...{I'm gonna walk down to electric avenue and I'm gonna say ' have you got PAT testing records for all that mate'}
- Messy
- Grand Shidoshi
- Posts: 3588
- Joined: Wed Dec 27, 2006 8:59 am
- 17
- Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.
Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment - Location: Sunny London where the streets are paved with gold ;)
- Has thanked: 369 times
- Been thanked: 663 times
Re: Foyer sofa
This guidance is a legacy measure from the FP Act guidance. Something to consider was receptions used to be a desk, some chairs and a typewriter. Now there will be at least one pc, tv's, printer, scanner and coffee machine.
I rarely see a reception without these items and in many cases they are unacceptable in a protected route.
Then if there's a lobby approach where there is more than one staircase, you don't have to discount a staircase when determining the max occupancy figure.
Placing a combustible reception in these circumstances may lead to inadequate capacity in the alternative staircase where the other is now untenable due to a reception fire
Risk is more complicated than applying rigid rules, so a reception may be possible. It's just a little tricky in some circumstancrs
I rarely see a reception without these items and in many cases they are unacceptable in a protected route.
Then if there's a lobby approach where there is more than one staircase, you don't have to discount a staircase when determining the max occupancy figure.
Placing a combustible reception in these circumstances may lead to inadequate capacity in the alternative staircase where the other is now untenable due to a reception fire
Risk is more complicated than applying rigid rules, so a reception may be possible. It's just a little tricky in some circumstancrs
- abarnett
- Snr Member
- Posts: 544
- Joined: Fri Sep 18, 2015 2:01 pm
- 8
- Twitter: @adb82
- Industry Sector: Warehousing
- Occupation: QHSE Co-Ordinator
- Location: South Queensferry
- Has thanked: 3 times
- Been thanked: 16 times
Re: Foyer sofa
Interesting that the signage says to keep clear yet there are the sofa and table.
Looking at it in isolation, it would appear that the table is providing an obstruction to the escape route (assuming the doorframe to the right of the picture)
Also, in isolation, assuming this is the only escape route from upstairs then I'd be loath to have a source of fuel there.
For me the mitigating factors in terms of risk would be sources of ignition and what the detection system is - but I'm no fire expert!
Looking at it in isolation, it would appear that the table is providing an obstruction to the escape route (assuming the doorframe to the right of the picture)
Also, in isolation, assuming this is the only escape route from upstairs then I'd be loath to have a source of fuel there.
For me the mitigating factors in terms of risk would be sources of ignition and what the detection system is - but I'm no fire expert!
Safety doesn't happen by accident