How many fire exits needed - Ground floor office
Moderator: Moderators
How many fire exits needed - Ground floor office
hi, first post with general fire exit question.
i appreciate that this is difficult to visualise without picture but but i have a question regarding fire exits.
The building i work in is a low rise (ground floor only) rectangular modern building with one entry/exit at each end of the building, these are the the only 2 external doors in/out - each entry serves as final exit which leads into large open space car park at each end.
Basically a large bungalow with a door at each end!
The building has a central corridor (approx 25M) running from one door to the other with individual offices off the central corridor. Halfway down the corridor is a door marked "fire door" which is a substantial fire door that is always closed, but not locked.
Here's the issue - we wish to move in to one end of the building and lock the "middle" door with a view to leasing out the other half of the building to a new company - essentially then creating 2 buildings within one. Each end would have its own external door/exit and would essentially become a dead-end style building - the distance from the external door to the furthest office is not more than 12M.
No more than 12-15 people would work at each end of the building, the building is used for light office duties, has no machinery etc and otherwise is fire compliant.
Can you tell me, would it be legal to lock the internal fire door and thereby creating 2 separate offices, and what the reference for this is? My understanding is because the building is low risk, low rise with low population 1 final exit is sufficient?
Thanks
Denzil.
i appreciate that this is difficult to visualise without picture but but i have a question regarding fire exits.
The building i work in is a low rise (ground floor only) rectangular modern building with one entry/exit at each end of the building, these are the the only 2 external doors in/out - each entry serves as final exit which leads into large open space car park at each end.
Basically a large bungalow with a door at each end!
The building has a central corridor (approx 25M) running from one door to the other with individual offices off the central corridor. Halfway down the corridor is a door marked "fire door" which is a substantial fire door that is always closed, but not locked.
Here's the issue - we wish to move in to one end of the building and lock the "middle" door with a view to leasing out the other half of the building to a new company - essentially then creating 2 buildings within one. Each end would have its own external door/exit and would essentially become a dead-end style building - the distance from the external door to the furthest office is not more than 12M.
No more than 12-15 people would work at each end of the building, the building is used for light office duties, has no machinery etc and otherwise is fire compliant.
Can you tell me, would it be legal to lock the internal fire door and thereby creating 2 separate offices, and what the reference for this is? My understanding is because the building is low risk, low rise with low population 1 final exit is sufficient?
Thanks
Denzil.
Re: How many fire exits needed - Ground floor office
I would go along with your findings on this because the single travel distance is less than 18 mtr's and the maximum number is well below 60 in each office. Does the office have a manual call point system or automatic fire detection?
How would you let the other office know that there is a fire in your side or visa versa. Also there would be a legal requirement to co-operate and co-ordinate, you would need to ensure the change is covered in your FRA. aslo the new company moving in would need to carry out their own FRA and communal areas would need a fire risk assessment carried out by the owner of the building if such a situation arises
Red
How would you let the other office know that there is a fire in your side or visa versa. Also there would be a legal requirement to co-operate and co-ordinate, you would need to ensure the change is covered in your FRA. aslo the new company moving in would need to carry out their own FRA and communal areas would need a fire risk assessment carried out by the owner of the building if such a situation arises
Red
- Keith1983
- Suitable and Sufficient since 1983
- Posts: 8330
- Joined: Mon Dec 08, 2008 3:08 pm
- 15
- Industry Sector: Engineering/Manufacturing/ Construction
- Occupation: H&S Coordinator
- Location: Lincolnshire / South Yorkshire
- Has thanked: 34 times
- Been thanked: 24 times
Re: How many fire exits needed - Ground floor office
Why not let the other company use the corridor as a means of escape? After all you could have it closed and alarmed so that if anyone went through it an alarm would be activated therefor letting the everyone know it had been breahed. I presume at night the individual office doors are locked so should be no security issues and the alarm would stop people opening the door for fun. That way security is maintained and so is an alternative means of escape for both seperate companies.
So when the whole world is safe..............what are we going to do then?
Re: How many fire exits needed - Ground floor office
Thanks, very helpful.
regarding fire alarms, there are 2x maunal fire alarms at each end of the building that link into the same system.
Take your point about revising the FRAs.
Do you have the reference that refers to the 18M / 60 pax rule? I've only ever seen this referred to on various websites not the actual line or law.
Thanks again,
D.
regarding fire alarms, there are 2x maunal fire alarms at each end of the building that link into the same system.
Take your point about revising the FRAs.
Do you have the reference that refers to the 18M / 60 pax rule? I've only ever seen this referred to on various websites not the actual line or law.
Thanks again,
D.
Re: How many fire exits needed - Ground floor office
Keith1983 wrote:Why not let the other company use the corridor as a means of escape? After all you could have it closed and alarmed so that if anyone went through it an alarm would be activated therefor letting the everyone know it had been breahed. I presume at night the individual office doors are locked so should be no security issues and the alarm would stop people opening the door for fun. That way security is maintained and so is an alternative means of escape for both seperate companies.
if you can do what keith has suggested then it would do no harm but from a fire safety point of view it would not be required and could be simpler to assume the door is in fact a solid wall as the travel distance would still be acceptable. Also could be an issue that if one office is closed (locked up) and the other office tries to evacuate through the locked office they may not be able to escape from the building as the doors could be securely locked. Doors only need to be readily openable during hours of occupation.
Re: How many fire exits needed - Ground floor office
there is no specific law on this but the HM goverment documents would bee seen as recommendation or good practice. it's free to download or £12 to buydenzilW wrote:Thanks, very helpful.
regarding fire alarms, there are 2x maunal fire alarms at each end of the building that link into the same system.
Take your point about revising the FRAs.
Do you have the reference that refers to the 18M / 60 pax rule? I've only ever seen this referred to on various websites not the actual line or law.
Thanks again,
D.
http://www.communities.gov.uk/publicati ... afetyrisk2" onclick="window.open(this.href);return false;
Travel distance are given on page 68 maximum 60 persons for one exit is on page 87. 60 people applies in my mind if you are talking of a room or ground floor with only one final exit. More than 60 people then a second exit would be required all other means to allow for more (fire alarm, sprinklers, additional fire compartment etc etc)
red
Re: How many fire exits needed - Ground floor office
Again, really helpful thanks.
Ref the other guys coming through our corridor, this isn't an option as we double lock the exterior door with enhanced security and it is alarmed etc; the cost to convert would be very expensive.
thanks for the help guys. cleared this up nicely.
Ref the other guys coming through our corridor, this isn't an option as we double lock the exterior door with enhanced security and it is alarmed etc; the cost to convert would be very expensive.
thanks for the help guys. cleared this up nicely.
- Messy
- Grand Shidoshi
- Posts: 3592
- Joined: Wed Dec 27, 2006 8:59 am
- 17
- Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.
Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment - Location: Sunny London where the streets are paved with gold ;)
- Has thanked: 373 times
- Been thanked: 669 times
Re: How many fire exits needed - Ground floor office
You should have a look at ADB (approved document B) of the building regulations for further info. The standards in ADB apply during construction or alterations. If the aim is 2 x completely separate occupancies, the corridor should perhaps be made up with a 60 min stud wall. *(subject to the last paragraph below)
Means of escape wise, it doesn't sound problematic. Two points though:
1) If you have a manual fire alarm system and the panel is in demise 1, how are those in demise 2 going to access it to reset on those occasions when demise 1 is unoccupied? in addition, I don't think BS5839-1 (BS refers to fire alarm design) will allow one system covering two occupancies where those occupancies are completely separate. This might cause enforcement issues, but I haven't got my 5839 copy available to check.
2) Be careful about occupancies and purpose groups. ADB requires 1hr fire resistance between occupancies in some circumstances. A locked 20 minute or 30 minute fire door obviously will not achieve this
* If you are not using an architect or approved inspector, I would recommend a fire safety consultant be appointed to check over the proposals, as with the best will in the world, to give definitive advice blind and via the interweb is a bit of a lottery
Means of escape wise, it doesn't sound problematic. Two points though:
1) If you have a manual fire alarm system and the panel is in demise 1, how are those in demise 2 going to access it to reset on those occasions when demise 1 is unoccupied? in addition, I don't think BS5839-1 (BS refers to fire alarm design) will allow one system covering two occupancies where those occupancies are completely separate. This might cause enforcement issues, but I haven't got my 5839 copy available to check.
2) Be careful about occupancies and purpose groups. ADB requires 1hr fire resistance between occupancies in some circumstances. A locked 20 minute or 30 minute fire door obviously will not achieve this
* If you are not using an architect or approved inspector, I would recommend a fire safety consultant be appointed to check over the proposals, as with the best will in the world, to give definitive advice blind and via the interweb is a bit of a lottery
- Jack Kane
- HSfB Site Grand Shidoshi
- Posts: 25077
- Joined: Wed Mar 17, 2004 12:13 am
- 20
- Twitter: https://twitter.com/hsfb
- Industry Sector: Manufacturing Subsea XTs
- Occupation: Senior HSE Advisor for TechnipFMC & HSfB Founder
- Location: Sunny Bo'ness
- Has thanked: 254 times
- Been thanked: 199 times
- Contact:
Re: How many fire exits needed - Ground floor office
Hey Denzil, welcome to the forums
Glad to have you with us.
Glad to have you with us.
RoSPA Awards Ambassador and Mentor #RoSPAAwards #HSfB #Proud
There is no such thing as a "stupid" or "daft" health and safety question!
- Alexis
- Official HSfB Legend
- Posts: 48868
- Joined: Thu Mar 18, 2004 10:52 am
- 20
- Twitter: https://twitter.com/AlexisHSfB
- Location: West Lothian
- Has thanked: 2867 times
- Been thanked: 341 times
- Contact:
Re: How many fire exits needed - Ground floor office
Hi Denzil, welcome from me too.
"A candle loses none of its light by lighting another candle."
Hundreds of FREE Health & Safety Downloads Here
Hundreds of FREE Health & Safety Downloads Here
-
- Newbie
- Posts: 18
- Joined: Mon Mar 29, 2010 9:34 am
- 14
- Industry Sector: Housing, Construction, Regulators
- Occupation: Building Control Professional & Fire Safety Consultant, "Fire Risk Assessment Team Leader".
- Location: Leighton Buzzard, Beds & Haringey, London
Re: How many fire exits needed - Ground floor office
Hi,
The answers are in Vol 2 of the Approved Document for Fire Safety in the Building Regualtions 2010.
In brief, if work-place (office, workshop, retail shop) has less than 18m travel distance (from all points where persons may be in the event of a fire) to a final exit, then ONE exit is acceptable. (If that exit door width is only 800-1000 wide then the limt would be under 60 persons.)
You will need to get a Building Regualtions approval for the proposed "Material Alteration" (i.e. the sub-division of the building into two units and the closing up of the alternative exit) to this building. Becasue without additional measures you may be making the future means-of-escape worse than it already is.
But, show any Building Control body, that you also have a suitable and sufficient fire alarm for both sub-units, and small enough max travel distances, and you should get a approval certificate in a flash!
The answers are in Vol 2 of the Approved Document for Fire Safety in the Building Regualtions 2010.
In brief, if work-place (office, workshop, retail shop) has less than 18m travel distance (from all points where persons may be in the event of a fire) to a final exit, then ONE exit is acceptable. (If that exit door width is only 800-1000 wide then the limt would be under 60 persons.)
You will need to get a Building Regualtions approval for the proposed "Material Alteration" (i.e. the sub-division of the building into two units and the closing up of the alternative exit) to this building. Becasue without additional measures you may be making the future means-of-escape worse than it already is.
But, show any Building Control body, that you also have a suitable and sufficient fire alarm for both sub-units, and small enough max travel distances, and you should get a approval certificate in a flash!
Last edited by HelenPJ on Thu May 12, 2011 12:32 am, edited 1 time in total.
Reason: Removed signature details - please note that Signatures are subject to the Forum Terms & Conditions of Use and are not enabled through your User Profile until you have at least 40 posts. Thank you
Reason: Removed signature details - please note that Signatures are subject to the Forum Terms & Conditions of Use and are not enabled through your User Profile until you have at least 40 posts. Thank you
- hammer1
- Grand Shidoshi
- Posts: 2617
- Joined: Sun Oct 15, 2006 4:59 pm
- 17
- Industry Sector: Commercial, residential, construction
- Occupation: Health, Safety and Fire consultant
- Location: Sunny South London
- Been thanked: 46 times
- Contact:
Re: How many fire exits needed - Ground floor office
I do not think Building Regulations come into this issue as there is no new build or major physical alterations. It seems they are just splitting a ground floor office area into 2 with no alterations apart from locking a door. I might be wrong but I think building control may not get involved, worth giving them a ring though to confirm. Only say this as I have seen buildings change in this way with building control not bothering to get involved, however as with fire authority I find each building control officer has different views to the next one.
What you should be doing is reviewing your FRA (as you employ more than 5 persons it is recorded?).
Record the travel distance from the corner of your office to the final exit? Is it in line with guidance that allows a single escape route?
What are you occupancy levels ?
Is it open plan office?
What current, if any AFD system have you got? If it is only a ground floor building, then I would assume you have no AFD system in place
Have you extinguishers?
Liaise with new tenants on other side. request their FRA, ensure your fire emergency plan is communicated, share fire drills etc.
If fire door is to be secured, ensure all staff are made aware, any signs rmeoved.
With not knowing the full details, I would assume this would be ok so long as you conduct a FRA ensuring the above questions are answered.
What you should be doing is reviewing your FRA (as you employ more than 5 persons it is recorded?).
Record the travel distance from the corner of your office to the final exit? Is it in line with guidance that allows a single escape route?
What are you occupancy levels ?
Is it open plan office?
What current, if any AFD system have you got? If it is only a ground floor building, then I would assume you have no AFD system in place
Have you extinguishers?
Liaise with new tenants on other side. request their FRA, ensure your fire emergency plan is communicated, share fire drills etc.
If fire door is to be secured, ensure all staff are made aware, any signs rmeoved.
With not knowing the full details, I would assume this would be ok so long as you conduct a FRA ensuring the above questions are answered.
The song goes...{I'm gonna walk down to electric avenue and I'm gonna say ' have you got PAT testing records for all that mate'}