Escape route / angle of diversions...

Discuss all things fire related and emergencies of all kinds.

Moderator: Moderators

User avatar
hammer1
Grand Shidoshi
Grand Shidoshi
Posts: 2617
Joined: Sun Oct 15, 2006 4:59 pm
17
Industry Sector: Commercial, residential, construction
Occupation: Health, Safety and Fire consultant
Location: Sunny South London
Been thanked: 46 times
Contact:

Re: Escape route / angle of diversions...

Post by hammer1 »

Paul1979 wrote:Hi hammer, yes refurbishment about 3 years ago...not sure about building controls but would they have signed off occupancy levels too?
If your looking at occupancy levels then 60 persons is single MOE, where alternative MOE is in place then the 45 degree angle needs to be assessed to see if the alternative MOE can be used. If not then look at what compensatory measures are in place and look to see if you want to use ADB or BS9999 as your guidance tool.
The song goes...{I'm gonna walk down to electric avenue and I'm gonna say ' have you got PAT testing records for all that mate'}
baywaves
Student
Student
Posts: 65
Joined: Thu Oct 14, 2010 1:16 pm
13
Been thanked: 2 times

Re: Escape route / angle of diversions...

Post by baywaves »

There is only one exit from that main room.

A fire in the lobby will trap everyone.
User avatar
hammer1
Grand Shidoshi
Grand Shidoshi
Posts: 2617
Joined: Sun Oct 15, 2006 4:59 pm
17
Industry Sector: Commercial, residential, construction
Occupation: Health, Safety and Fire consultant
Location: Sunny South London
Been thanked: 46 times
Contact:

Re: Escape route / angle of diversions...

Post by hammer1 »

baywaves wrote:There is only one exit from that main room.

A fire in the lobby will trap everyone.
That's why it should be a protected lobby to prevent fire developing in first place.
The song goes...{I'm gonna walk down to electric avenue and I'm gonna say ' have you got PAT testing records for all that mate'}
baywaves
Student
Student
Posts: 65
Joined: Thu Oct 14, 2010 1:16 pm
13
Been thanked: 2 times

Re: Escape route / angle of diversions...

Post by baywaves »

I agree with you that "Zero tolerance in the lobby area is a must".

But its a social club being used for cafe / restaurant / bar, and you know as well as I do, that it doesn't matter if its 'officially' declared as being a protected lobby, some idiot will think its a good idea to put a Christmas tree in there, or a drinks machine, a photocopier or something similar.

Then there's the other discussion to be had - "Is the ground floor lobby protected from the staircase"?
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Escape route / angle of diversions...

Post by Paul1979 »

Hi, the staircase isn't protected at ground floor level at all. The ground floor is open plan restaurant / cafe. There are FDs to the kitchen and staff areas. But the staircase is open until you reach the first floor where the Georgian wired fire doors are.
baywaves
Student
Student
Posts: 65
Joined: Thu Oct 14, 2010 1:16 pm
13
Been thanked: 2 times

Re: Escape route / angle of diversions...

Post by baywaves »

Well that's not good.

So are you saying that if any fire occurred on the ground floor, the smoke from that fire would go up the open stairway to the Georgian wired fire doors on the first floor.

Bye the way, where has the floor plan gone?. I can't see it anymore in this thread.
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Escape route / angle of diversions...

Post by Paul1979 »

Hi Bywaves,

I'm not sure what happened with the floor plans so I've re-attached them. I've also included one for the ground floor. The staircase shown on the ground floor is internal and leads up to the Georgian glazed fire doors on first floor.

The staircase at ground floor level is open and discharges in to the cafe / restaurant seating area. So the staircase is protected at the top by the fire Georgian double doors.

All doors on the ground floor [kitchen and staff room] are fire doors with 30-min rating. So if a fire occurred on the ground floor [seating area] yes, it would allow smoke to travel up to the Georgian glazed doors. But if a fire occurred in the main hazard [kitchen] it is contained.

The building regs and local F&RS haven't commented on protecting the staircase at the bottom with a lobby.

Let me know what you think and many thanks for all your help.
Attachments
Ground floor plan
Ground floor plan
First floor plan
First floor plan
User avatar
bernicarey
Anorak Extraordinaire
Anorak Extraordinaire
Posts: 8973
Joined: Tue Jan 13, 2009 2:50 am
15
Twitter: @bernicarey
Industry Sector: Consultancy/Training
Occupation: Safety, Health, Environment and Fire Consultant.
Location: The heart of the East Midlands...
Has thanked: 76 times
Been thanked: 300 times
Contact:

Re: Escape route / angle of diversions...

Post by bernicarey »

So if a fire did break out in the Kitchen, admittedly the most probably place (although we can't discount an electrical event anywhere), the entire place has to get out via the main entrance?
This really does not give me a comfortable feeling.

I can't spend any longer looking at this right now, but I'll be extremely interested in others comments.
www.belvoirsafety.co.uk

Tomorrow - your reward for being safe today...

Image
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Escape route / angle of diversions...

Post by Paul1979 »

If a fire broke out in the kitchen, occupants upstairs could use the alternate external staircase.

Occupants downstairs would typically use the main entrance. Occupants in the kitchen could also use the fire exit from the kitchen.

[apologies, the plans are just drawn up on excel so fairly basic]
User avatar
hammer1
Grand Shidoshi
Grand Shidoshi
Posts: 2617
Joined: Sun Oct 15, 2006 4:59 pm
17
Industry Sector: Commercial, residential, construction
Occupation: Health, Safety and Fire consultant
Location: Sunny South London
Been thanked: 46 times
Contact:

Re: Escape route / angle of diversions...

Post by hammer1 »

Paul1979 wrote:If a fire broke out in the kitchen, occupants upstairs could use the alternate external staircase.

Occupants downstairs would typically use the main entrance. Occupants in the kitchen could also use the fire exit from the kitchen.

[apologies, the plans are just drawn up on excel so fairly basic]
Oh didn't know 1st floor has an alternative MOE, so does the kitchen ground floor, so your real concern then is occupancy levels for the 1st floor, remember to discount a MOE as it is not lobby protected.

You know AFD coverage? is it category L2 system installed?

That the thing with these types of threads hard to ascertain when you not been to site ;) goes without saying any assumptions should be taken as that .salut
The song goes...{I'm gonna walk down to electric avenue and I'm gonna say ' have you got PAT testing records for all that mate'}
User avatar
Messy
Grand Shidoshi
Grand Shidoshi
Posts: 3585
Joined: Wed Dec 27, 2006 8:59 am
17
Occupation: 46 years experience with a metropolitan Fire Brigade and then Fire Safety Manager for a global brand.

Now sort of retired from the fire safety game, but doing the odd job here and there to keep my grey matter working and as I hate sudoku and havent got the back for an allotment
Location: Sunny London where the streets are paved with gold ;)
Has thanked: 363 times
Been thanked: 660 times

Re: Escape route / angle of diversions...

Post by Messy »

I am much more relaxed about this one. Unless I have missed something, it seems to me that the travel distance from the furthest point upstairs to the flat roof is around 18 to 20m. At that point you have two MOEs which are separated by the fie doors at the top of the stairs.

I am not sure what all this talk of protected lobbies is about as you cannot have a protected lobby unless it leads into a protected escape route that remains protected to the final exit. That is not the case here. I am assuming the route over the flat roof to the ground is satisfactory, lit by maintained EL and edge protected

I may restrict numbers unless the so called lobby entrance was widened, but I cannot be sure from the details supplied

The condition & maintenance regime of the of the doors should be strict as they are critical.

Good training and regular drills, would help lower the risks
User avatar
Paul1979
Member
Member
Posts: 291
Joined: Mon Oct 24, 2016 4:19 pm
7
Industry Sector: Property Management including H&S
Occupation: Property Manager including reviewing of H&S assessments and implementing remedial actions...or trying to justify why they are over the top and an alternative solution can be found!!
Location: London
Has thanked: 204 times
Been thanked: 44 times

Re: Escape route / angle of diversions...

Post by Paul1979 »

Hi messy

Yes, travel distances are ok - no more than 18m from any point in the room to either the double FDs at top of stairs, or the fire exit to the flat roof. They have AFD and EL and the flat roof is edge protected. The metal staircase is a bit of a mess and they're storing rubbish underneath it!!! But that can be fixed and will have to be monitored daily.

The main and original question was whether it was seen that there is one MOE from the room, or two? As the FDs to the stairway and the fire exit door to the flat roof are very close together. If you stand in the main room, the angle of diversion is less than 45 degrees...

So should the occupancy be limited to that of a one door room meaning it is 60? My feeling is that if a fire occurred in the space outside of the room, then BOTH exits would be blocked, which could potentially lead to 60 trapped people??

The fight between the FRS and the council licencing guy is still ongoing by the way....at present the client is restricting numbers upstairs to 60 as a safe guard.
Post Reply

 